Boiling summer is just few weeks ahead, scheduled and unscheduled power cuts are expected as usual. Inverters are one of the most demanded products of summer season. Are you planning to buy or upgrade your inverter in this season? Then instead of being trapped in the marketing gimmicks, understand some basic facts and do a little bit home work. Here some facts you must know before buying an inverter
Calculate your power requirements
Before going to purchase an inverter- You have to make a rough estimation of your power requirements. remember- Inverter is not a Generator. Inverter has it’s own limitations. You can’t power and run your complete home with a normal inverter. If your power requirement is more than 3000 VA, then an inverter alone can’t cater your demands effectively. No doubt a high power inverter can run your refrigerator and air conditioners, but how long? Here your battery will not last more than few hours. Hence it it better to go for a home generator. However if you don’t want a single minute power downtime, then a power inverter – electric generator combination is a good option.
Wattage rating of typical home appliances
| Appliances | Power |
| Fan (Ceiling) | 50-75 Watts |
| Fan (Table) | 25-50 Watts |
| CFL 18 Watts | 18 Watts |
| Computer (Desktop) | 80- 150 Watts |
| Laptop | 20- 75 Watts |
| LCD TV (32”) | 150 Watts |
| Refrigerator | 160 – 250 Watts |
| Tube Light (4 Feet) | 40 Watts |
Starting power and running power
Starting and running power requirement of all electric appliances are different. An 18 Watts CFL takes around 25 Watts power to start and after few seconds it stabilizes to 18 Watts. Some appliances like Refrigerator, Washing Machine etc take almost double power to start as compared to the normal running power. Hence before selecting an inverter you must calculate the starting power requirement also.
Difference between VA and Watts
Often people confuse with the difference between Watts and VA ratings of inverter or other home appliances. Manufacturers use both these terms according to their requirements to confuse and mislead the consumers. Power drawn by the equipment (Power using equipment like Bulb, Fridge, Washing Machines, ACs, Stabilizers etc.) and Power generated by the equipment (Generators, Inverters, UPS etc) can be expressed in Watts or VA (Volt Ampere). In general Power generating or stabilizing equipment manufacturers use the term VA to specify their ratings and power consuming products use Watts to specify their ratings. Here comes the difference. Power in Watts is the real power drawn or supplied by an equipment, this is the real value. VA is the apparent power (more theoretical) which is obtained by multiplying the Voltage and Current drawn/supplied by an equipment. We can equate the VA and Watts ratings:
Power in Watts = Power in VA- Losses
or
Power in Watts = Power in VA x Efficiency of the equipment
The ratio of Power in Watts to Power in VA is termed as Power factor. Unfortunately manufacturers often don’t specify the power factor or efficiency in their products.
Let’s see an example. You are purchasing an inverter with 650 VA power ratings. This 650 VA indicates, it can supply 650 VA power under ideal situations( means efficiency of the inverter is 100%). If we take 80% as a typical efficiency figure, the said inverter can supply 80% of 650 = 520 Watts only. Now you can understand why inverter manufacturers only publish the VA rating on their products. If an inverter or UPS is coming without mentioning power factor, you must take a safe value of 0.6 (60%) as power factor while connecting appliances.
Inverter or Home UPS?
Nowadays we can see a new segment in inverter market- Home UPS. Functionally both inverter and UPS do the same job- Converting Direct Current from batter to Alternating Current which is used as a backup power generating device in case of mains power failure. UPS as the name suggest provide Uninterrupted Power Supply to equipment. The equipment will not feel the switching delay from mains to UPS supply. Switching over time of a typical UPS is 3 to 5 Milli Seconds only. A standard inverter takes around 500 Milli seconds which is unacceptable for the electronics devices like computers, Modems, Routers, printers etc.
Home UPS is a combination of Inverter and UPS. Here the switching delay of inverter has been brought down to UPS standard. Hence you need not to go for a separate UPS for PCs and associated devices. One thing you must remember- UPSs are further classified in to three- Offline, Online and Line interactive. Home UPS are normally Offline only, hence they cannot replace your online UPS requirements to drive sophisticated devices.
Digital Inverter
What is digital in inverters? First generation inverters were using power transistors as switching devices and transistorized circuitry for monitoring/controlling applications. That is an old story. Nowadays inverter technology has changed a lot. A complete transition from old square wave technology to Pure Sine wave technology with the help of advanced Digital Signal Processing (DSP) techniques. Micro controllers are extensively utilized for précised monitoring and controlling applications. Switching transistors are replaced with high efficient MOSFETs.
Battery
Batter- the vital part of inverter. Performance and life of an inverter is greatly depends upon battery. We can see several classifications of inverter batteries. Normally high power Lead Acid batteries are used to power inverters. Lead acid batteries are classified in to different types as per application, design, technology etc.
Battery Capacity
Capacity of a battery is expressed in terms of Ampere Hour (Ah). It indicates the rate of current a battery can supply for a given duration. If the capacity of a battery is 100 Ah, that battery can supply 100 Ampere current for 1 Hour or 1 Ampere Current for 100 Hrs, 2 Amps Current for 50 Hrs .Capacity of inverter batteries are generally 100 Ah, 150 Ah or 180 Ah.
Why automotive batteries are not suitable for inverters?
Lead acid batteries used for automotive purpose are termed as “High Cycle” lead acid batteries. These batteries are designed to provide high current for a very short duration (To start the vehicles). Automotive lead acid batteries are not designed to be regularly discharged by more than 25% of their rated capacity. Here the requirement of inverter is totally different. Inverter require “Deep Cycle” type batteries to provide continuous power which can be discharged at least 50% of their rated capacity. Some good deep cycle batteries can be discharged over 80% of their capacity. Deep Cycle batteries have specially designed thick plates to withstand frequent charging and discharging.
Maintenance Free batteries
Lead acid batteries require regular maintenance. You have to check the electrolyte level and require to be topped up on regular intervals. Moreover these batteries release poisonous gases during charging and discharging. If you don’t keep the batteries in a properly ventilated place, it can invite serious health problems. You have to keep the terminals of normal lead acid batteries corrosion free by applying petroleum jelly or grease regularly.
Maintenance free batteries are sealed lead acid batteries which do not require topping up or additional ventilation.
Disadvantages of Maintenance free batteries:
- Cost of Maintenance free batteries are very high as compared with normal lead acid batteries.
- Life- Life of maintenance free batteries are comparatively low. For example if a normal lead acid battery run for 3 years, you can expect 2 years from a maintenance free battery.
- Scrap value- You will not get much more from a maintenance free battery as scrap.
If you like a fit and forget inverter system or your situations don’t permit you to do periodic maintenance of batteries then go for a maintenance free battery. Let me quote one example- My friend uses Maintenance free batteries in his home because his old aged mother is living alone and she don’t have enough knowledge on battery maintenance. In that situation maintenance free battery is a right choice.
Tubular batteries
This is the most popular segment of inverter batteries-Tubular batteries have several advantages compared to flat plate batteries. More complex design increases the manufacture cost but the high electrical efficiency and extra long life make tubular batteries suitable for both domestic and industrial applications. A good maintained tubular battery can run unto 8 years or more. Tubular batteries comparatively require less maintenance. Cost of tubular batteries can go up to double of a normal flat plate battery, however if you have a high efficiency inverter then go for a tubular battery, you will not regret. Almost all popular battery brands in India like Exide, Prestolite, Amaron etc have specially designed tubular batteries for inverters.
Batteries from Inverter manufacturers
We can see that almost all inverter manufacturers supplies battery along with inverter. I strongly suggest-don’t go for such batteries. This is a simple business technique, often they just market batteries on their brand name. As battery costs more than inverter, it is always better to go for a reputed and trusted battery brand. I have personal experience with Exide and Prestolite tubular batteries. Exide Invatubular batteries run flawlessly upto 5 years.
Local made batteries
We can see a common trend- People often go for branded inverter and local battery combination. Local batteries costs around 60% of the cost of same rated tubular batteries. However I don’t recommend local batteries because of the following reasons:
- Poor life: A well maintained local battery can run maximum up to 3 years.
- Poor efficiency: Electrical efficiency of local batteries are very poor, which requires more time to charge.
- Safety hazards: Lead acid batteries are very much prone to explosion if not maintained well. We have witnessed several battery explosion incidents. Poor quality of safety vent plugs, casings, impure lead and acids increase the chances of accidents.
- More maintenance: We can see that local batteries require more maintenance because of poor efficiency.
Warranty/Guarantee of Battery
First of all understand the difference between Warranty and Guarantee- Under the terms of Warranty you will get the maintenance and repair of items in free of cost but no replacement. A product under Guarantee will be get replaced in case of malfunctions. Normally we can see batteries are marketed under guarantee + warrantee combination , ie first few years Guarantee and after that warranty. Some brands offer even 48 months warranty. As battery is the costly and vital part of your inverter system, go for a brand which offer long term guarantee/warranty and after sales support.
Inverter output (Sine wave, Square wave, Stepped Sine wave)
Our commercial power supply is 50 Hz pure sine wave (see the figure). However most of the inverters don’t output pure sine wave. Old inverters generate 50Hz square wave or 50Hz modified Sine wave (Quasi Sine wave , Trapezoidal wave or Stepped Sine Wave). Then the question comes. This wave shape really matters? Yes it does.
All commercial instruments are designed to run on pure sine wave. Characteristics of such devices are greatly depend upon the input wave shape. A change in wave shape will affect the performance of the appliances. Appliances like Motors, refrigerators, Ovens etc will generate full power on pure sine wave input only. Distortion in the sine wave creates humming noise in transformers, and audio devices. Some instruments like light dimmers, few battery chargers, toasters etc require pure sine wave to work. Prolonged operation of appliances in Square or stepped waves will considerably affect the life of such equipment due to the generation of heat.
You may be noticed that audio amplifiers, Televisions, Fluorescent lamps etc make noise on inverter power. This indicates that inverter output is not pure sine wave. Sine wave inverters are costly as compared to square wave and stepped sine wave inverters, however it is always advisable to go for a pure sine wave inverter for the safety and effective performance of your appliances.
| Square Wave | Stepped Sine Wave | Pure Sine Wave | |
| Safety of Appliances | Less | Moderate | High |
| Life of Appliances | Less | Moderate | High |
| Battery Life | Less | Moderate | High |
| Noise Level | High | Moderate | Normal |
| Heat generation | High | Low | Normal |
| Suitability for sophisticated appliances | No | Not recommended for prolonged use | Yes |
Inverter efficiency and No load power consumption
Efficiency of an inverter is proportional to the amount of power drawn. It can varies from 90% to 50% from full load to light load. Here the notable factor is that inverter efficiency is high on maximum load. Generally an inverter is in its most efficient capacity when being used at around 1/3 to 3/4 of it’s full rating.
Power Consumption of inverters
Inverters take mains power supply to charge the batteries. If the charging section of an inverter is not energy efficient, it will waste electricity even after the battery is fully charged. This will inflate your electricity bill. It is very difficult to check this aspect in shop before purchasing an inverter. However you can test the same at your home. Switch off all appliances except the mains supply to inverter, disconnect the battery and measure the power consumption for a specific period.
Battery backup duration
Here we have an equation to find the battery life on load
Time(in Hrs) = Battery Voltage (In volts) * Battery Capacity (in Ah)*efficiency of inverter
Load (in VA)
Let us have a sample calculation
Battery voltage = 12 Volts
Battery Capacity = 150 Ah
Load = Two fluorescent lamps (40 Watts each) and one ceiling fan (75 Watts )= 155 Watts
Inverter efficiency = 80%= 0.8
Backup Time = 12 * 150*0.8/155= 9.29 Hrs (Approx)
Other features
Solar Panel input: In typical Indian situations even eight hours of continuous commercial power supply availability can not be assured. Hence many people use the most reliable and alternate non conventional power source- Solar energy. Nowadays inverters facilitates the usage of Solar Panels also. Those inverters are embedded with solar charging circuits and regulators.
LCD Status Indicators: Modern inverters come with LCD status indicators to display various status like Battery charge level, Load, Input/Output voltages, Battery life etc.
Voltage stabilizer , High/Low voltage cutoff : Normal inverters don’t stabilize the mains supply, means the commercial supply is routed directly to the appliances without monitoring. Some inverters comes with in built voltage stabilizer , which protects your appliances from voltage fluctuations.
Earth Leakage Protection: Earth leakage protector is a safety device used to protect users from electric shock and appliances from damage. Modern inverters come with in built earth leakage protection circuits, which continuously monitor earth leakage and cut off the supply to safeguard the users.
After Sales Support
We can’t give a blanket suggestion in favor of a particular brand or model. All electronics equipment are prone to damage, hence after sales support is always paramount which varies from place to place. As inverters are static devices, go for a dealer or brand who offers on site warranty repair and maintenance.
{ 189 comments… read them below or add one }
Next Comments →
That was a real comprehensive overview of invertors. I bought a sine wave invertor some months back, without an UPS, and I noticed that sometimes the switching over causes the computer to shut down, sometimes it causes it to restart, and sometimes it doesn’t affect it at all, working like a UPS. Wonder why this variation in switchover delay behavior.
Hi
sir i have 2.5kv UPS i m not able to run my laser printer what may be the problem please suggest me sir
It is not advisable to connect a laser printer with a conventional UPS.
1. Laser printers take heavy current while printing. Heater of the Laser printer is supplied with a pulsed current. The sharp rise and fall of this spike constitute heavy current flow , often normal UPS can’t supply that much current for the small duration.
2. If your UPS output is not pure Sine wave, then the Laser printers may not work properly.
A really good overview on inverters. A personal opinion about sales and service, I find USHA very prompt ,particularly in kerala compared to other brands.
This article has answered just about every question I had about buying an inverter/ battery. Thank you!
It’s actually a great and useful piece of information. I’m glad that you shared this useful information with us. Please keep us up to date like this. Thanks for sharing.
SF Sonic battery- Power house 1500
my inverter is 850va SEBZ (microtech)
for load – 2FAN (92W each)
back up is only 3.5hrs .
but as per your calculation, it would be at least 7Hrs.
time=(12V*150AH*0.8)/(2*92)=7.5Hrs
what wrong with my system
or suggest some better battery/inverter for more back up time
Probable problems.
1. Battery efficiency poor, it is not giving the rated output.
2. High inverter loses.
Thanks for sharing this valuable information. I would like to mention few small things: There are various battery brands available such as:
SF Sonic, Exide, Amaron, Amco, Okaya, Prestolite, Panasonic VRLA SMF batteries, I – Plus SMF VRLA batteries, Li – Ion batteries, Ni-Cad batteries, Ni-MH Batteries, Integrated solar batteries, UPS – SMF VRLA Batteries, TELECOM (CFP Type) etc.
Thanx for your valuable comments. One more thing I would like to mention that there are number o battery brabds one can go for: SF Sonic, Exide, Amaron, Amco, Okaya, Prestolite, Panasonic VRLA SMF batteries, I – Plus SMF VRLA batteries, Li – Ion batteries, Ni-Cad batteries, Ni-MH Batteries, Integrated solar batteries, UPS – SMF VRLA Batteries, TELECOM (CFP Type)
Hi veryuseful info indeed. one doubt is how come in formula of battery back up, Inverter VA does not play any role.
No.. inverter VA does not play any role in battery backup, however we can see that inverter efficiency is maximum in half to full load. A 300 VA inverter running with two fans (More than half load) can give more backup than a 600 VA inverter in the same battery.
Hi Sujith,
Thanks for your information about inverters.
I am planning to buy inverter for house –Sine wave Inverter of 600VA /100AH battery.
How about Microtek Inverter -Sine wave 600 VA and exide/sonic battery 100 AH for one LCD TV,3 fan,one tubelight,3 CFL.
Any idea about HBL battery(Hyderbad battery limited)Please comment on Microtek/Exide service in Kerala
Thanks
Riaz
Go for at least 600 VA will not be sufficient for this load .Don’t expect more backup with a 100Ah battery.
Service is mainly depends upon the efficiency of service centers in your locality.
Hi Sujith,
Thanks….
But Sujith ,actually we are not going to use all the appliances at a shot.So what you suggest.We have to keep in mind the price also ….
one more thing….Please comment on HBL battery…how is its performance….
Regards
Riaz
Then it’s OK.You can comfortably run your LCD TV, one Fan and two to three CFLs
sir,
i have a n APC BI 850Sine model home ups with AMCO TAFE 180Ah tubular battery. one year seven months old.
only providing 3.5 hours backup for just 2 cieling fans. what to do please help. invertor was once replaced for same complaint but not solved, please please please help!!!!!!!
The problem may be with battery. It has been observed that people get tap water instead of distilled water (Buy distilled water from reliable vendors only), it cause permanent damage to battery plates. Get your battery checked.
thanx and sorry to disturb you again sir, but
sincebought i am only using distilled water brought from market and this problem is there since newly bought, please suggest a way out
Hi Sujith,
I am planning to buy an inverter with battery to run 3 Fans, 3 tube lights and 1 TV with a backup of 5-6 hours. Kindly suggest which brand of inverter and battery will be best?
Thanks:-)
i am planing to buy a exide 820VA inverter. this is new in d market. i want to know if it has voltage stabilizer? becoz in d pick hours in my area voltage is 100-120 nomally.so i need a fast charging inverter so that it can easily charged in low voltage also.
HI SIR- Whats the difference between using 850VA inverter with 100 Battery , or 650 inverter with 150 .. Whats the best combination and how the relationship between battery and inverter is understood for best efficiency.
In an 850 VA Inverter and 100 Ah battery combination you can use more devices simultaneously, but the backup will be less. In a 650 VA inverter 150 Ah combination, the back up will be more.
Here the batter Ah is the deciding factor of backup time.
thanks , your reply is really valuable
hii sir,which flat plate battery should I purchase for the 760VA Inverter(capacity of battery in plates)??
Go for 150 or 180 Ah Tubular battery
Not only there is specific Inverter Battery but there are different brands which belongs to Inverter Battery like: Lead-Acid Inverter Battery, Tubular Inverter Battery, SMF Inverter Battery etc.
Hi,
My Requirements is around 400 – 450 Watts. So i decided as per your calculation that i need. i Have 3 fans and around 8-10 CFL’s.. Thats my requirement.
around 650VA inverter. My calculation suggests that i would need around 350 AH battery if i want a 6 hours backup. Please advice me if my calculation is correct.
Also, For Installations – Can i point out which electrical points i need to be powered up. Does it require separate wiring to light up specific points.
Now, Can you also suggest what battery types i need to choose.. tubular/inva and so on
Thank you very much.
No such 350 Ah battery commercially exists. Maximum capacity of lead acid battery we can see is 180 Ah. If you want to run 3 fans and 8-10 CFLs simultaneously for 6 hrs then go for an inverter with 24 Volts input. Normal low wattage inverter (ie 650 VA) don’t have the charging section to charge high rated batteries. Hence go for a high ended inverter which needs 24 Volts input.
Hi,
I have regular 850VA inverter and 100Ah SONIC battery.
Can I use solar panel (say 100 Wp) to charge my battery (using charge controller)?
Thanks.
sir please tell me
i want to buy an inverter for load 4 fans 3cfl 1 tube what should be the rating of inverter and battery. is 750va inverter is ok then wat should be the rating of battery.
thanks
which is best inverter of 750va for home use
mension name of company plz reply
hi Sujith,
if u plz suggest a brand for 800watt inverter(UPS),i woul be really greatful to u………………………………plz reply…………………
Hello Sir,
i bought one inverter of 12v 65AH with 50 volt solar panel, we have power cut of 8 hours during the day time , we use 11w cfl *2 nos and 1 fan( 42 inches) , we use the power after sun set , it works only 6 hours only, we have local battery, i would request you to suggest , on the battery and should i increase the panel form 5ovolts to 100 volts , kindly help me out.
regards
joseph
Sir can i get a reply soon aspossible
thanks
You can do the following
Use a 100 or 150 Ah battery. In that case you have to increase the capacity of your solar panel from 50 Watts to 100 Watts ( You have mistaken- it’s Watts not Volts). See an ebay listing.
http://www.ebay.in/itm/Solar-Panel-12-Volts-100-Watts-Polycrystalline-Cells-/160823187295?pt=LH_DefaultDomain_203&hash=item2571cf175f
hiii sir this is ramakrishna, i want to buy an inverter for my home i need 3 fans& 6 tube (4FEET) lights please suggest me which is suitable for my requirement
hi Sujith
Thanks for really nice and elaborative article. I bought 800VA su-kam inverter (digital home UPS) along with su-kam normal battery 150Ah 6 years ago. su-kam battery lasted 3 years, then i bought a local tubular battery(kay cee) 170AH, it has also lasted 3 years, but now backup is very less , a single ceiling fan runs only 3-4 hours. Now I am planning to buy new tubular battery, first i was thinking to go for amaron 150Ah tubular or exide inva tubular, but on inquiry one shopkeeper told me that Microteck tubular is the only battery with laminated plates, it will last much longer then others, now I am confused, and also in tubular of exide or amaron etc there are different models with different warranty eg 24+12 or 36+12 months, please help me to chose good battery, as to go for exide IT , amaron or microteck, and also tall tubular or short tubular, and should go for longer warranty period or not
Thanks in advance
Hi Sukhwinder Singh, It’s nice to know that the article was helpful to you. One thing should always keep in mind while selecting battery, It’s a proven fact is that some local battery brands perform equally good as branded batteries. The only thing is that we have to identify the right local brand. Let me quote an example. In Amritsar a local battery brand named “India” is selling like hot cakes. A 180 Ah tubular battery costs only Rs 7000 to 8000/- with two years of replaceable warranty . Moreover if you return the battery after the useful life you will get a scrap value around Rs 2000/-. Even if the battery run three years then also this is much better than the branded batteries.
In your case your local battery did run around three years, means it’s almost a good local brand. If the price difference from branded battery of same rating is in the range of Rs 4000 to 5000 and they give two years replacement warranty, then in my opinion it is a better option to go for your local brand.
Hello sujit, thanx for reply,
the price of this local brand is arond 10.5 to 11k, where as that of amaron is around 12k and that of exide is 13.5 to 14k. do there is not much price difference, but my friend got inva tubular 5 years back stll running fine, but heard that after sale service of exide is not good. how is mtek power brand of microtek, I think previously it was okaya.
No doubt Exide invatubular is a best battery and if maintained properly cost effective too. After sales service varies locally. I don’t recommend Okaya because my Okaya battery didn’t last even two years same thing happened to my friend too, he finally approached consumer court to get the battery replaced within warranty period.
dear sir,my name is rohit.i want to buy new 850va sine wave microtek inverter and old 75ah two exide battery for 2 ceiling fan & 2 cfl.plz tell me how long its backup.
Old inverter is OK but It’s very difficult to say about an old battery.
Dear Sujit Sir very-2 thanks for helping us. In these days electricity cutt-off is vey high in my area so i want buy a inverter that is give backup minimum 4 hours for 2 ceiling fan & 3 cfl under the 15000 range. I like microtek inverter & exide tubler battery but i confuse to how much va & ah i buy that is complete my this requirement.plz help me. i wait ur respective answer.
A 650 VA inverter will be sufficient in your case. Go for a 150 or 180 Ah battery as per your budget more Ah means more backup.
It is a good article. I am looking for an inverter to support 3 pc’s with 15″TFT monitor for 1 hour backup. I was looking at 1.5kva inverter with 2X12v 100Ah(or 150Ah) lead acid battery. After reading ur article it looks like its better to have tubular battery. But you have also mentioned (in the table) that tubular batteries have low safety. How come? Why? Is my configuration ok.
Thanks in advance
All batteries except Sealed Maintenance Batteries have safety issues means Acid split, poisons gas escape etc. However if you keep the tubular battery in a well ventilated dry place then you can almost ignore that safety point.
1.5 KVA and 2×12 Volt 150 Ah combination is is enough for three PCs with TFT monitors. It can run flawlessly more than 1 Hr.
Thanks for the prompt response. What parameter I should change to support 4 pcs instead of 3. Thanks.
Sujith
Hi
I am getting lucas Power Guard, 150AH tubular with 2 years immediate(without sending back to manufacturer) replacement warranty in 11.5K, how do you think about lucas brand, i think it is very old and reliable brand.Any Idea?
Thanks
Hi Sujit sir thanks 4 helping us.plz tell me that microtek inverter is best or exide inverter is good.plz suggest today I will buy this depending ur decision.
Go for Microtek inverter Exide Tubular combination..
Dear sir,
my requirtment is 02 tubes,1 celling fan, 1 computer with lcd led monitor, i m confused please tell me whose inverter or battery buying me.
Hi..
Sir, I want to buy a Microtek 650VA digital inverter. Just to operate 1 tubelight and 1 ceiling fan and occasionally a PC for one hour back-up. Can I go for 80ah exide battery for this inverter? Is there any safety precautions in using lower ah batteries with digital inverters?? One of my friends told me to be so.. due to the quick charging property of the digital inverters.. Plz suggest me.
Extremely low capacity battery and a high ended inverter is not a good option because nowadays most of the modern inverters are designed for faster charging to tackle frequent and lengthy power failures. High charging currents can deteriorate the performance of low rated batteries and it’s a safety hazard too. However you can connect an 80ah battery for this inverter but think about the backup time.
sir can you provide some information regarding amaron tubular tall and short flat tubular batteries.how do amaron fair against exide tubular battery it 500 range and what are the prices of amaron tubular batteries.i tried to check the website of amaron but there is no information provided but only model numbers of batteries why . When were these amaron tubular batteries launched and should i buy one instead of exide.
Dear Sujith,
I need to puchase an inverter good quality with low price /low maintenance, can you help me for that ?
Regards
Mohanan
Most of the modern digital inverters are maintenance free, but batteries are not. You will get a good digital inverter in the range of Rs 3500-4500. Just do a little bit market survey about the after sales service. Microtek, Luminous,APC, Sukam, Usha etc are the examples of trusted brands
dear sir you havnt replied to my query
Sir, I am using Canon Image Class MF 4350 d printer , One Computer , One Tube Light, Two Fans in my office. I am planning to purchase 1450 VA “Exide ” inverter and 12V tubular batteries 2 nos. I use my printer very rarely on my inverter. Is this capacity full fill my requirements. Please advise.
I Want to know that which battery is most suitable with 850va inverter.
Is it 180Ah, if yes then why or if no then why.
No such Ah suitability. It’s depends upon your requirement. More Ah means more backup. If you need more backup, go for a high Ah battery. If you are in an area of frequent power failure even more than 6 hrs a day, go for a fast charging inverter else high capacity battery will not get enough time for full charge which can reduce the life of battery.
Thanks for quick reply.
I am from PALI rajasthan, power cut here is now a days about 2 hours, in summer it rises up to 6 hours a day. Please suggest us a pure sine wave inverter (850va) & battery combination.
Hi Dear Sir, I m Vijay from Mumbai. I want to buy 450+ 135Ah Invared Tubular Exide Battery & 850 Vh Sine Wave Microtek Inverter. Please tell me that how long its backup for two ceiling fan & two 40w tubelight. I wait ur respective reply after it I buy this.
&
How its cost.
Hi Sujith,
i hav an apc 850 inverter supported by 120ah battery. last week i got a replacement of my old with a new piece of inverter along with a new battery(prestolite, same specs), thanks to tech team who was not able to identify issue and hence i got both as replacement. However ,due to a power shutdown ystdy here, i just received a backup of just 3hrs, which is quite abnormal, considering both peices are good. Do you think it can be an issue again with a battery?Please advise.
Thanks
What was the load? Have you done inverter wiring properly? Check for leakages.
it was just a fan which was running, any thoughts.? their own technician had comeover to do the wiring.
sir i have 4 desktop computer with led screen + 2, 36wat tube lights + one fan + one ink jet printer . what capacity of inverter and battery is good for me , i need only 3-4 hours back up. Please also suggest brand and aproximate cost.
Thanking you
Hi Dear Sir, I m Vijay from Mumbai. I want to buy 450+ 135Ah Invared Tubular Exide Battery & 850 Vh Sine Wave Microtek Inverter. Please tell me that how long its backup for two ceiling fan & two 40w tubelight. I wait ur respective reply after it I buy this.
&
How its cost.
Sir can you give market feedback of SU-Kam shiny 650VA inverter?
Dear Sujith,
Pl suggest me the best (inverter+battery) combination with make which would run 3 fans, 2 nos of 60w cfls and a 40″ LED 3D tv for atleast 3 hrs.
Thanking you,
sir,i want buy 450+ 135ah invared tubular exide battery or 850vh sine wave microtek inverter plz suggest how long its run for 2 ceiling fan & 2 cfl
Hi Sujith, I want to use SOLAR-PANELS with some 180 ah battery with out using electricity connection at all. If it is possible for the batteries totally depending on the solar-panels for charging. My question is can I use the current from the solar-panel at day-time, at the same time charging the batteries for use at night. Is this possible?
@ Sammy.
You can charge a 180 Ah battery with solar panels without depending power grid. It is always better to use a high wattage solar panel for fast and effective battery charging. We can’t expect optimum output from a solar panel always. A 400 Watts 12 Volt solar panel can give 400/12 = 33Amps current. A 180 Ah, 12 Volt battery requires 30 Amps current to get charged in 6 Hrs.
Hence you have to use minimum 400 Watts solar panel for charging. If your budget permits go for a 1 KW panel. You can’t use the current directly from solar panel at day time, however can run DC fans, and DC LED/CFL lights directly with these panels. It’s much effective than inverters.
Thanks Sujith. I appreciate for your quick reply and ‘valuable suggestions’. Your blog made me think in good way of saving electricity and mainly money.
I think I’ll go for 1kw or more. Thanks once again.
Hi sujit, thanks for your valuble information regarding inverters
I want to purchase 850 VA inverter and 150 AH. Batter. for my home
for 3 celing fan & 5 cfls .can u suggest me weather 650 VA inverter with 180 AH battery will be best choice.
Are these batteries use ful for charging through solar pannels in future i want to shift to solar power as an alyernate power .
Thanks and regards
D .Ramesh chandra
Hi Ramesh,
It is better to go for 850 VA 180Ah combination. You can use the same battery for solar panels in future. If you have such a plan then it is a nice idea to go for an inverter with inbuilt solar charge controller.
Hi, sujit
thanks for your valueble suggesion
hi sujit i want buy 135ah exide invared tubler battery & 850vh sine wave microtek inverter for 2 fan & 4 cfl plz tell that how long hours its run.
plz plz tell ur valuable reply………….